#182185 - 11/20/08 02:22 PM Does 310.15 overrule temperature limitations?
Mills Offline
New Member
Registered: 09/24/04
Posts: 5
Loc: Carolina
I can't seem to reconcile T 310.15(B)(6) with 110.14(C)(1)(b)(1). What do you think?

This is a residential single phase overhead service drop, going to a GE meter center with feed thru lugs. The 200A main will protect the feeder to a 200A subpanel inside. Local jurisdiction using 2005 NEC.

Does 2005 NEC T310.15(B)(6) allow 4/0 Al for service and feeder, or is that trumped by the manufacturer’s label [Use 60/75C conductors], which would require 250 kcmil?

Thanks,
Mills
Top
Featured Tools
#182187 - 11/20/08 03:04 PM Re: Does 310.15 overrule temperature limitations? [Re: Mills]
gfretwell Moderator Online   content
Member
Registered: 07/20/04
Posts: 4210
Loc: Estero,Fl,usa
Two different things.
310.15(B)(6) gives you a break on the ampacity because they know there is a lot of diversity in the total load of a dwelling. You are not using 310.16 at all.
_________________________
Greg Fretwell
Top
#182221 - 11/21/08 07:25 AM Re: Does 310.15 overrule temperature limitations? [Re: Mills]
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 979
Loc: Chesapeake, VA
Originally Posted By: Mills
Does 2005 NEC T310.15(B)(6) allow 4/0 Al for service and feeder, or is that trumped by the manufacturer’s label [Use 60/75C conductors], which would require 250 kcmil?
The safe bet is always to ask your AHJ as theirs is the only opinion that matters, but I concur with Greg, 310.15(B)(6) requires 4/0, and specifically states you don't have to go larger. 310.16 does not apply to this cable.
Top


Featured:

2008 NEC & Related Books, Tabs, CD-ROMs & Exam Prep Study Guides
2008 NEC & Related Books, Tabs, CD-ROMs & Exam Prep Study Guides


Tools for Electricians
Tools for Electricians

 * * * * * * * * Licensing Info and Lookup
Licensing Info
& Lookup

 

Recent Posts
OT:Menus
by gfretwell
01/06/09 11:32 PM
Sizeing a whole house generator
by gfretwell
01/06/09 11:27 PM
17KW Free Standing Range
by Eddy Current
01/06/09 08:43 PM
Required Sign Circuits
by HotLine1
01/06/09 03:34 PM
Ice Storm Surge?
by SteveFehr
01/06/09 12:16 PM
Top Posters (30 Days)
gfretwell 49
renosteinke 49
Trumpy 48
HotLine1 40
pdh 28
January
Su M Tu W Th F Sa
1 2 3
4 5 6 7 8 9 10
11 12 13 14 15 16 17
18 19 20 21 22 23 24
25 26 27 28 29 30 31

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals